When through concrete slab repair is required?

When through concrete slab repair is required?

When through concrete slab repair is required?

(OP)
It's well known that if deteriorated area of concrete slab is larger than a certain amount, a through slab repair is required.
This criteria doesn't really convince lots of engineers. When, then, a through slab repair is required from an engineering view point?

RE: When through concrete slab repair is required?

Not sure what you mean by "through slab repair". Must not be "well known".

RE: When through concrete slab repair is required?

hokie66: I think the OP is referring to 'through-thickness' (i.e. full-depth) slab repair, as opposed to partial-depth repair.

Alan CA: If the damaged area is both large (in area) AND more than 50% of slab depth, it if often then a candidate for full-depth repair - BUT this is also influenced by the technique of concrete removal.

For example, if concrete jack hammers are used and the slab is rather thin, then such a technique cannot tolerate more than about 50% of slab thickness removal without damaging the good remaining concrete.

However, is hydrodeomolition is the concrete removal technique, then you may be able to justify greater slab depth removal/repair before you consider full-depth removal and replacement.

If also depends on the type of slab: one-way, 2 way, post-tensioned (especially unbonded PT), and also temporary shoring, existing reinforcement, etc.

Also depends on the cause of the damage (water intrusion, freeze-thaw, chloride, ASR etc etc), and the expertise and experience of the contractors too.



RE: When through concrete slab repair is required?

To add to Ingenuity's good response, with thicker slabs I have encountered situations where the top 4" is removed for a top surface delamination and the bottom 3-4" is removed for a soffit delamination, leaving a thin unreinforced area. Not good (unless you are the Contractor getting paid to do the work), and a really expensive way to repair a reinforced concrete structure. Through slab repair for sure when soffit and top surface deterioration coincide.

RE: When through concrete slab repair is required?

(OP)
Thank you very much for your answers.
Yes, here in Canada a full-depth slab repair is called through-slab.
The reason behind my question is that sometimes you sound the cracked slab with a hammer to hear something hollow or sense large vibration, yet the recommendation is a top surface repairs or soffit only!
Other cases involve a slab that is cracked across its depth, and still you see a recommendation of top or soffit repairs only! I'm not convinced that this should be the proper case!

RE: When through concrete slab repair is required?

Quote (Alan CA)

Other cases involve a slab that is cracked across its depth, and still you see a recommendation of top or soffit repairs only! I'm not convinced that this should be the proper case!

A “slab cracked across its depth” - do you mean a flexural crack only, because if so, and there is no resulting spall, epoxy injection is a common repair technique, assuming the crack is dormant.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

White Paper - The Evolving Landscape of Commercial Battery-Powered Trucks
What’s driving the evolving landscape of truck electrification? What are the barriers, motivators and strategies for accelerating the electric transition? What insights and resources are available for today’s design engineers working to achieve industry disruption and evolution? For answers to these and other pertinent questions, read this white paper. Download Now
eBook - Rethink Your PLM
A lot has changed since the 90s. You don't surf the Web using dial-up anymore, so why are you still using a legacy PLM solution that's blocking your ability to innovate? To develop and launch products today, you need a flexible, cloud-based PLM, not a solution that's stuck in the past. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close