Contactor performs better at switching current than carrying current
3

Contactor performs better at switching current than carrying current

Contactor performs better at switching current than carrying current

(OP)
We are running a cyclical test that involves turning on a 12VDC 100W incandescent lamp (8A nominal, up to ~20A inrush) for 3s every 8s. The primary switch for this is a MOSFET inside a control board.

The lamp circuit resistance is measured in between cycles using a milliohm meter, which is done using a 23A-rated electromechanical contactor (Allen Bradley 100-C23EJ10) to switch out the power circuit, and a smaller relay to switch in the measuring circuit. Both the positive and negative leg of the lamp are being switched. The contactor was programmed to stay switched-in whenever the resistance was not being measured, and the MOSFET would do the actual lamp switching.

After about 150k cycles we started to see lamp faults more and more frequently (using current detection), which would stop the cycle. Taking no action except restarting the cycle allowed the test to carry on, anywhere between a dozen and a few hundred additional cycles.

Finally I changed the program so that the contactor was doing the actual switching rather than the MOSFET. Since then the test has run uninterrupted for over 60k additional cycles and counting.

I am aware of wetting current, i.e. that there is a minimum current needed to break through the oxide layer of non-noble metal contacts. 8A should be plenty, let alone the additional inrush transient. I believe, but could not verify, that there is also a minimum voltage for wetting to work, but it would seem that if no current is flowing due to oxide then there would be 12V across that contact, which is plenty to break through the oxide.

So why is the contactor more reliable when it is doing the switching, rather than just the carrying, of the lamp current??
Replies continue below

Recommended for you

RE: Contactor performs better at switching current than carrying current

2
Vexing.
As I understand your post, The contactor is held closed all the time and the current is switched on and off by another device.
A couple of points strike me:
The first is the inrush. You are using a factor of 2.5 for the inrush. An old rule of thumb for incandescent inrush was a factor of 10.
Contactor rating. The contactor should have an incandescent rating.
This contactor appears to be rated for incandescent loads up to 18 Amps so you should be good with an 8.3 Amp lamp.
This contactor is approved/rated for voltages from 200 Volts to 690 Volts AC. I don't see any ratings for lower voltages DC.
But why is the contactor failing open?
Back in the day when we first started working with solid state logic devices, a rule of thumb, borne out by practical experience was that contact film rendered pilot switches unreliable when used at voltages below 100 Volts.
This may be mitigated to some extent by contact wipe on better quality devices.
Note that it was voltage and not current that we considered when faced with contact film issues, albeit with much lower current levels.
Contact wipe:
A device with contact wipe is designed so that the contacts close with a slight sliding action. The contacts are designed so that there is a slight movement of wiping action between the position of first contact and the final seated position.
In a contactor this may be accomplished by arranging the contact carrier so that in the open position the contacts are slightly off parallel. As the contactor closes the contacts first make slightly off parallel. As the contactor moves to the seated position, the contacts move to a parallel position with a slight wiping action.
There are other means of providing contact wipe.
By keeping the contactor closed, you are not getting the benefit of either contact wipe nor the burning action of the inrush that may be of the order of 80 Amps.
Your observations seem to support this theory.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Contactor performs better at switching current than carrying current

Is the coil getting the full rated voltage? It may be that the contacts aren't closed with sufficient force.

RE: Contactor performs better at switching current than carrying current

(OP)
Thank you for the responses so far. Point by point:

I do not have a schematic, I'll see if I can mock up something quick.

The "faults" come from a current detection circuit looking at lamp current. If current is less than ~1A for more than 0.5s while the lamp is on a fault is generated.

The inrush is due to the DC power supply which has active current-limiting. The PSU runs a total of 3 lamps. The current is limited to ~50A, 50/3=17A.

I didn't look at DC voltage ratings for this contactor, but it should work. The main issue with DC current and relays/contactor is the pull-out, since any arcing will not necessarily self-extinguish, unlike AC power which does so every half-cycle.

I cannot speak to the internal construction of the contactor; presumably all of this has been taken into account.

Before the program change the contactor did still switch every cycle, it was just switching off back on while the lamp remained off.

The coil is an electronic coil that draws much less current than a standard coil. This allows direct wiring from a standard PLC discrete output rather than through an interposing relay. I have just verified that it is seeing 24V. Also it continues to make the typical loud "clunk" every time it actuates.

RE: Contactor performs better at switching current than carrying current

Quote (OP)

The main issue with DC current and relays/contactor is the pull-out, since any arcing will not necessarily self-extinguish
I have seen that. I was called to a small electric crane with the complaint that the hoist brake would not apply.
The brake coil was energized by a small relay.
Someone replaced the relay with an AC rated relay. This was a good quality double pole, double brake relay, but not DC rated.
Both poles were in series.
What happened is that the relay struck four arcs across the four circuit break points. The current was low but the persistent arc eventually melted the silver alloy contact material. When the contact surfaces melted the metal flowed together and completed the circuit.
At that time the arc was shunted by the molten metal bridges which then cooled and solidified.
I no longer have the photograph of the four small silver alloy hour glass shapes.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Contactor performs better at switching current than carrying current

However, this is supposedly happening without the contactor actually opening at all.

Nevertheless, there does seem to be something about DC currents that do bad things with contacts; I've had similar problems with a torchiere floor lamp that had a DC driven bulb, and after a certain amount of operating time, the bulb connection to its socket would degrade. I had thought that one might be able to switch the DC every so often to mitigate that, but never got around to it.

TTFN (ta ta for now)
I can do absolutely anything. I'm an expert! https://www.youtube.com/watch?v=BKorP55Aqvg
FAQ731-376: Eng-Tips.com Forum Policies forum1529: Translation Assistance for Engineers Entire Forum list http://www.eng-tips.com/forumlist.cfm

RE: Contactor performs better at switching current than carrying current

It's oil or contamination on the contacts. Possibly, even from their own manufacture or internal factory lube. Running them as dry contacts (original scheme) never allowed the oil to burn-off so eventually they became 'insulated'. Now that you're running them 'not dry' that can not happen.

Keith Cress
kcress - http://www.flaminsystems.com

RE: Contactor performs better at switching current than carrying current

My EYES!!!!!




Otherwise thanks for the schematic. Glad using the contactor is working for you. Happy I don't have to listen to it. I think I'd have used a light sensor to tell if the filaments had fried. LOL

Keith Cress
kcress - http://www.flaminsystems.com

RE: Contactor performs better at switching current than carrying current

I'm wondering why you are doing this. If you are testing the life span of the lamp this may not be real world conditions. The lifetime of the lamp when subject to the normal x10 inrush may not be as great as when the inrush is limited to x2.5.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Contactor performs better at switching current than carrying current

(OP)
Hey I said it was rough! tongue

We are actually interested in the contacts going to/from the lamp, not the lamp itself. We have done separate tests in the past to measure lamp degradation. Yes the lamp is part of the measuring circuit but only out of necessity.

RE: Contactor performs better at switching current than carrying current

I think you have your answer already. If your contacts are not switching they will eventually fail open when used for low voltage DC.
If you want to measure the contacts under real world conditions it may be better to actually switch the full inrush current.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Contactor performs better at switching current than carrying current

(OP)
Waross, This is the full inrush current in this application. We use that same DC power supply in production, so the inrush is always limited.

I agree, I think I have my answer, although I'll have to ponder this a little longer to fully digest it.

Thanks everyone!

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close