PI vs PD for position, speed, force, current control

PI vs PD for position, speed, force, current control

PI vs PD for position, speed, force, current control

(OP)
Dear all,
I have a question regarding using PI or PD control based on the control variable. Is there a relation? As I found a lot of people use PI controller for speed or current control for servo systems. However, PD is used a lot for position or force control. I am wondering if there are reasons for that or recommendations for the type of the control based on the control variable and the application.

RE: PI vs PD for position, speed, force, current control

If there is a double integration in the plant under control -- for instance, from a torque/force command thru velocity to position -- you need derivative action to get the damping required for stability. Proportional gain here is just a spring (no shock absorber -- the car suspension analogy is a good one here).

If there is only a single integration in the plant under control -- for instance torque/force to velocity, or voltage command to current thru an inductive load -- you do not need derivative action. The system is much more inherently stable.

Curt Wilson
Omron Delta Tau

RE: PI vs PD for position, speed, force, current control

(OP)
Many thanks Curt. You provided me with very useful information. where can I read more about these about these recommendations for PT, PID and PD.
Regards,

RE: PI vs PD for position, speed, force, current control

Read modern control engineering by ogata. it is a very useful book.

RE: PI vs PD for position, speed, force, current control

(OP)
I have Ogata, but I can't find these information

If there is a double integration in the plant under control -- for instance, from a torque/force command thru velocity to position -- you need derivative action to get the damping required for stability. Proportional gain here is just a spring (no shock absorber -- the car suspension analogy is a good one here).

If there is only a single integration in the plant under control -- for instance torque/force to velocity, or voltage command to current thru an inductive load -- you do not need derivative action. The system is much more inherently stable.


I am wondering about guidance for when each type is used

RE: PI vs PD for position, speed, force, current control

Many textbooks talk about the "type" of the physical system. A "Type N" system has N integrations (poles of the system at the origin of the S-plane).

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close