Jed, you are so right! That contractor does not know what he is doing. In addition to the problems you have noted, the average placement rate for the 150 yd
3/hr pump (running full bore, non stop) is just 6 in/hr. Not good, since the idea of tremied concrete is to have a solid mass. The tremie pipe should be embedded at least 2 feet into the concrete that has not had its initial set - that's not going to happen here. Placement in layers is done sometimes, but is not the best practice.
A thickness of 4.5 feet is "thin" for tremied concrete, especially since there is so much volume to be placed. As noted above (pipe embedded 2 ft.) a good bit of the total thickness may be minimally acceptable (especially at the perimeter) even under the best of conditions.
The surface of tremied concrete typically has a slope of about 1:6 (it can range from 1:3 to 1:12). The 15 ft. grid you mentioned is just right to minimize this issue. Dragging the pipe horizontally through the concrete is a no-no. If the concrete could be placed fast enough (not going to happen with one pumper) the pipes could be "leap frogged" around the area (instead of having 30, or so, pipes on a 15 ft. grid.
A few other items:
Concrete mix with high cement content: often 6.5 to 7 bags cement per cubic yard (some may "wash out" during underwater placement).
High slump concrete: typically 8 inches (needed since vibration is not practical).
A temporary plug in the 10 inch diameter (minimum) steel (not aluminum) pipe at the beginning of placement. This is to ensure the first concrete deposited has not segregated.
In the concrete mix, use gravel (rounded) instead of crushed stone. Less flow resistance.
Are there any specs on tremied concrete in the contract?