Power Line Capacity Assessment

Power Line Capacity Assessment

Power Line Capacity Assessment

(OP)
WE are working on adding a redundant (M-T-M)substation to existing redundant 72 kV power line circuits, each uses 795 kcmil, "Drake" ACSR. Our load, when added, would result to a line estimated maximum electrical loading of 105 MVA at 72 kV during a CONTIGENCY CASE (WHEN THE BUE TIE IS CLOSED AND ONE POWER LINE IS SUPPLYING POWER TO THE ENTIRE LOADS).

The installed 72 kV circuits are Southwire 795 kcmil, "Drake" ACSR with the ACSR design specification as attached. The design basis for this ACSR was 100 Deg C Conductor temperature at maximum sag with ambient of 32 Deg C with wind and at 1,020 A load current.

However, I would think that when these power lines are already built, the capacity assessment would not use "design values" but worst case minimum. The ACSR data obtained from Southwire lists different ampacities at 100 Deg C conductor temperature and we are at a confusion and debate as which would be used.

Can we use 826 A for normal conditions and use 1060 A for CONTINGENCY CONDITIONS when one power line is down and all bus tie circuit breakers will be closed and one incomer open in all substations fed from these redundant lines?

Regards

RE: Power Line Capacity Assessment

What about your sag limits and the NESC limits?

RE: Power Line Capacity Assessment

You will need to ask the utility what their criteria is. Although the line may have clearances for operation at up to 100C, aluminum starts to loose strength when operated over 90C and many connectors are not rated for continuous operation at 100C. There may either be a lower temperature for normal operations or some other way to limit the loss of life of the conductor to a few 10s of hours per year. I have not heard of utilities in the USA using less than 0.6m/s of wind as the minimum wind speed in the ampacity calculations.

If the line has significant voltage drop or your operating voltage is less than 72 kV, you should also inquire whether the utility uses thermal limits in expressed in amperes or express as MVA calculated using nominal system voltage.

Are you in Canada or Scandinavia? 57N latitude drops your solar input a fair amount. Some utilities also use a time slightly later in the afternoon to coincide the typical maximum load/temperature of the day.

RE: Power Line Capacity Assessment

A quick reality check is to compare the voltage drop under load with the range of the on-line tap changer. The line capacity may be limited by maximum acceptable voltage drop rather than ampacity and sag.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Power Line Capacity Assessment

(OP)
HI Bacon4life, our installation is in Canada and the 72 kV power lines are not owned and operated by utility but by industrial plant customer (feeding mining area). Thank you for reminding us about the connector temperature limitations. Considering that our maximum loading happens in a contingency case, can we consider ampacity on a worst case 100 Deg C conductor temperature as our power line mechanical design and sag is based on 100 Deg C?

Waross, our tap changer AVR set point is set at 100% nominal 72 kV secondary, in this case I would think that our secondary voltage will be fixed at 100% nominal 72 kV at the transformer 72 kV bus.

Regards

RE: Power Line Capacity Assessment

As you increase the loading on the line the OLTC compensates to hold the voltage at the set point. Eventually, as the load continues to increase, you run out of taps and the voltage will start to fall. You may want to consider the lowest voltage that you are prepared to accept. You may find that this is the limit of your line capacity. It may be much much less than limits of ampacity and sag.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Power Line Capacity Assessment

I am not familiar with the Canadian codes covering industrial owned equipment. As a general concept, your approach to thermal limits may be reasonable, but it really depends on the owner and/or AHJ agreeing with your design philosophy. If the mine load was 24/7 with planned maintenance on the alternate 72 kV lines done at full load, I would be hesitant to go with 100C ratings. For variable residential/commercial loads where maintenance activities rarely coincide with system peaks, using 100C is more reasonable.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close