Techsan2013
Mechanical
- Aug 27, 2015
- 4
First off I understand that Hydrotesting over any substantial time period is erroneous as ASME guidelines state ~15min.
Per General Contractor/Contract with owner, we have to run a 24hr Hydrotest. The problem arises when they claim we fail the test and can't listen to reason, (temperature is going to affect the system).
I NEED an/a set of equations that account for the Thermal Expansion of the Pipe and the H2O, that can show that the system hasn't lost water. An equation that produces either Delta P, new P or a pressure correction factor could work.
I have a copper line 2" Dia. (Copper Type L)
Temp. int. = 92 F
Temp. fin. = 81 F
Pressure int. = 166 psi
Pressure fin. = 156 psi
-Thank you, from a frustrated PM.