Vacuum problem during start-up

Vacuum problem during start-up

Vacuum problem during start-up

(OP)
We are running a power station with two steam turbine units 360MW each. in which SEIMENS EMLO-F 2BE1 liquid ring vacuum pump installed two per each steam turbine unit. Normally with 2 pumps in service we are able to pull condenser vacuum from atm to 130mbara in 70 minutes. We had a problem last week during one unit start up where vacuum pulling process went very slow and it took almost 30 hours to reach 130 mbara. Finally the unit is back in operation and we are investigating the root cause. The main concern is that the issue is not resolved yet and we will face the same situation during any startup . we doubt the performance of the vacuum pumps or air ingress source to the condenser, based on the attached trend that shows the behavior of turbine exhaust pressure/vacuum pumps inlet and liquid ring temperature/turbine exhaust temperature.we did not make Helium leak detection test to check if we have air ingress. Appreciate your thoughts on which is more probable root cause (i.e issues with the vacuum pumps or air ingress).
Thank You
Replies continue below

Recommended for you

RE: Vacuum problem during start-up

In the absence of any mechanical work having been performed on turbines that would disturb correct function of seals etc., I'd check for under- or over-priming of the liquid ring.

CR

"As iron sharpens iron, so one person sharpens another." [Proverbs 27:17, NIV]

RE: Vacuum problem during start-up

Is the gland sealing system working correctly? Are you sure it is working correctly?

RE: Vacuum problem during start-up

(OP)
The steam turbine had major overhaul in April 2015, where all seals were reviewed and tolerances checked-we had few start ups without vacuum problems.
we are preparing for vacuum pumps capacity test this week.

RE: Vacuum problem during start-up

(OP)
regarding the sealing steam- higher steam flow than normal noticed during start up. it was strange to see the LP turbine exhaust temperature increasing to 60-70C just after charging the sealing steam header and starting the vacuum pumps. normally the LP exhaust temperature decreases with vacuum pulling.
also noticed the inlet temperature to vacuum pumps is 35 to 37 C while the LP exhaust temperature is 60-70C, the liquid ring temperature is 37 to 38C almost equal to or higher than the vac pump inlet temperature which is strange.
Thank you

RE: Vacuum problem during start-up

I recall one nightmare return-to-service which lasted days because we couldn't pull vacuum. We dismantled and recalibrated / rebuilt most of the gland steam control system before the mechanical group finally conceded that there was a problem elsewhere. They opened up the gland steam condenser, virtually at gunpoint, and discovered about 200lb of silt in the water side of the condenser. The machine behaved normally once that was sorted out.

RE: Vacuum problem during start-up

If your pumps were running warm you need to check that cooling system very aggressively.
These are liquid ring pumps, water forms the seal, you can't pump below the vapor pressure of the water in the pump.

= = = = = = = = = = = = = = = = = = = =
P.E. Metallurgy, Plymouth Tube

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close