TT system in fire risk environment

TT system in fire risk environment

TT system in fire risk environment

(OP)
MG book states that TT system isn't allowed to supply places with high fire risk, but doesn't give any reason, is there any?

RE: TT system in fire risk environment

Power0020,
What do you mean by MG book?
On a TT system if earth fault protection is provided by residual devices such as Current Operated Earth Leakage Circuit breakers
(ELCBs/ RCCBs) with 30mA trip threshold then there cannot be a fire risk. But if you provide earth leakage protection by overcurrent
devices then there can be a fire risk because the earth leakage current may not be enough to trip the overcurrent devices unless
you make sure that the "measured" earth fault loop impedance is less than 1666 OHMS to satisfy the allowable touch voltage
of 50V per IEC for 30mA threshold.

RE: TT system in fire risk environment

Power0020,
Due to high earth fault currents RCD devices are not allowed in TN-C systems. Per IEC60364, in a TN-C earthing system the earth fault current is
taken back to the source by the PEN conductor in contrast to PE conductor of a TN-C-S earthing system. That means at each utilization equipment,
the N terminal has to be bonded to the E terminal. With time if this bonding develops a high resistance to the earth fault loop impedance then,
the tripping time of the overcurrent device during an earth fault will be longer (more energy is released at the fault point) and it might
create a fire within the installation. Therefore, at installations or buildings where there is a fire risk, TN-C earthing is not acceptable.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close