Dear Geotechncial engineers,
I am plannning to coduct a pile load test , what is the suitable method? Kentledge with surcharge load or anchor pile method?
What are the advantages and disadvantages in using anchor method for vertical pile load tes?
Is there any techncial concern on using anchor method than sucharge load methos?
Regards
Balageotech
I am plannning to coduct a pile load test , what is the suitable method? Kentledge with surcharge load or anchor pile method?
What are the advantages and disadvantages in using anchor method for vertical pile load tes?
Is there any techncial concern on using anchor method than sucharge load methos?
Regards
Balageotech





RE: vertical pile load test by anchor method
If your pile has a very low design capacity, then using a dead load reaction (as you are calling "surcharge") can be done, keeping in mind that your dead load will have to be more than twice the design capacity of the pile since the load test should be done to twice the design capacity.
As your pile design capacity increase, using a dead load reaction system becomes increasingly difficult unless you have some very heavy equipment or other dead load reaction material that can be left in place for the entire length of the test and rebound.
Using reaction piles for the test usually works out better, but can be more expensive, since you'll be placing at least 2 reaction piles, (likely 4) so as to obtain adequate reaction for the test pile without failing the reaction piles in tension. Depending on soil conditions, a pile reaction system might not work because it depends on skin friction for its primary resistance.
RE: vertical pile load test by anchor method
Using the anchor piles for reaction for a friction (mainly) test pile, be aware that the proximity of the anchors to the test pile can have some bearing on the true support capability of the test pile. For instance compaction caused by displacement anchor piles near the test pile may occur and affect the validity of the test results. Spacing of the piles.
On the other hand using a dead-load as a reaction, does placing that load nearby compact the soil as a form of surcharge and also affect results of a friction pile?
RE: vertical pile load test by anchor method
RE: vertical pile load test by anchor method
www.PeirceEngineering.com
RE: vertical pile load test by anchor method