IBC/NFPA/IFC Question Emergency Generator Fuel Line in Parking Garage

IBC/NFPA/IFC Question Emergency Generator Fuel Line in Parking Garage

IBC/NFPA/IFC Question Emergency Generator Fuel Line in Parking Garage

(OP)
A client is contemplating re-routing his supply, return and vent lines through an underground parking garage to the emergency generator room. I do not see in the Code anywhere (Texas) that the fuel lines are required to be in a duct or separate pipe chase that has a fire resistance rating. Nor do I see anything that requires the fuel lines to be in a separate opening from the other pipes and conduits in the pipe chases in the garage. I would expect to see this for the parking garage but I checked in NFPA 110 and IBC 1305 and I do not see anything. Does anyone know whether there is a requirement for the pipe to have a fire resistance rating/be located in a duct?

Thanks!

RE: IBC/NFPA/IFC Question Emergency Generator Fuel Line in Parking Garage

Highstepper:

The requirements for the fuel oil supply and return piping are in two different codes. In my jurisdiction in Texas, we've adopted the 2012 International Mechanical Code, which has requirements in Chapter 13. Piping requirements are also found in 2012 IFC Section 5703.6. The IFC does not require piping to be in a rated shaft. IFC Section 5703.6.10 does require the piping to be welded when it is conveying a Class I liquid and the piping is located in a concealed space. Since this is a generator I'm assuming diesel fuel is the source of energy, which is a Class II liquid - so the section I cited is hopefully not relevant to your case.

RE: IBC/NFPA/IFC Question Emergency Generator Fuel Line in Parking Garage

(OP)
Thank you, Stookeyfpe! That is what I thought as well. I reviewed the Mechanical Code as well and came to the same conclusions. I just needed confirmation from others. I really appreciate your response.

Highstepper

RE: IBC/NFPA/IFC Question Emergency Generator Fuel Line in Parking Garage

You're welcome. Have a safe Memorial Day weekend.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close