AS3600 - Column or wall??
AS3600 - Column or wall??
(OP)
My post relates to the analysis of a vertical load bearing element under AS3600 (and beyond).
To my knowledge, AS3600 2009 does not define (for strength purposes) when a thin, long column 'becomes' a wall. This leave some ambiguity when analysing a vertical load bearing element of this shape.
For example:
- Take a vertical element 180mm x 720mm in cross section, with an effective height of 2400mm. The element is part of a braced frame and is loaded concentrically. The element is made up of 40MPa concrete, with reinforcement yet to be determined.
The designer appears to have two options;
1) Design the section as a wall - using clause 11.5.1 we end up with a capacity of about 1500kN (assuming min. eccentricity). This is independent of reinforcement. The designer adds some central mesh and that's it. The 'wall' takes 150 tonnes of load.
2) Design the section as a column - calculating the buckling load, slenderness and moment curvature interaction diagram and complying with the reinforcement detailing requirements for columns. For a column with say 1% reo (significantly more than the 'wall' above) the designer gets approx 500kN.
Finally - for those who tell me options 2) is correct; I'd like some back up. I know for a fact that there are numerous designs being certified and building today that use the 'walls' to support some big loads, and I love to argue the case!
Thanks,
To my knowledge, AS3600 2009 does not define (for strength purposes) when a thin, long column 'becomes' a wall. This leave some ambiguity when analysing a vertical load bearing element of this shape.
For example:
- Take a vertical element 180mm x 720mm in cross section, with an effective height of 2400mm. The element is part of a braced frame and is loaded concentrically. The element is made up of 40MPa concrete, with reinforcement yet to be determined.
The designer appears to have two options;
1) Design the section as a wall - using clause 11.5.1 we end up with a capacity of about 1500kN (assuming min. eccentricity). This is independent of reinforcement. The designer adds some central mesh and that's it. The 'wall' takes 150 tonnes of load.
2) Design the section as a column - calculating the buckling load, slenderness and moment curvature interaction diagram and complying with the reinforcement detailing requirements for columns. For a column with say 1% reo (significantly more than the 'wall' above) the designer gets approx 500kN.
Finally - for those who tell me options 2) is correct; I'd like some back up. I know for a fact that there are numerous designs being certified and building today that use the 'walls' to support some big loads, and I love to argue the case!
Thanks,
RE: AS3600 - Column or wall??
http://www.nceng.com.au/
"Programming today is a race between software engineers striving to build bigger and better idiot-proof programs, and the Universe trying to produce bigger and better idiots. So far, the Universe is winning."
RE: AS3600 - Column or wall??
How does the latest code stop a designer from doing this?
RE: AS3600 - Column or wall??
http://www.nceng.com.au/
"Programming today is a race between software engineers striving to build bigger and better idiot-proof programs, and the Universe trying to produce bigger and better idiots. So far, the Universe is winning."
RE: AS3600 - Column or wall??
RE: AS3600 - Column or wall??
asixth, I agree! But AS3600 is unclear.
If you were reviewing a design with this element designed as a wall, what would be your argument when push came to shove?
Thanks for the replies thus far.
RE: AS3600 - Column or wall??
RE: AS3600 - Column or wall??
I think the wall provisions He^2/(2500*tw) underestimates this. And a member such as 720x180 in my opinion needs to be designed as a column based on the dimensions alone.
RE: AS3600 - Column or wall??
- For the column/wall given in the OP, assuming pinned connections top and bottom, minimum eccentricity, 100% dead load, and M*1/M*2 ratio of -1, I get a column capacity(phi.Nu) of 1461 kN and wall capacity of 1489 kN. (1% reinforcement in the column, 0.15% in the wall)
- Applying the same method used by asixth in his last post, I get the stresses at maximum design load shown in the attached graph. For low slenderness ratios the column has a substantially higher design load, but for high slenderness the wall has a much higher design load. Given the lower reinforcement requirement, this doesn't make sense.
- I can find nothing in the code to indicate that the wall provisions are not applicable in this case, of for any wall with an effective height/thickness ratio less than or equal to 30, and low eccentricity applied load.
In summary, either the column provisions are over-conservative, or the wall provisions are dangerously un-conservative (or both). Either way, a revision of the code seems to be necessary. I will continue to use the column rules, but if presented with a column similar to the one described in the OP, designed to the wall provisions, assuming fire requirements were not applicable, I can't see any way in which it would be outside the code requirements.Doug Jenkins
Interactive Design Services
http://newtonexcelbach.wordpress.com/
RE: AS3600 - Column or wall??
Doug Jenkins
Interactive Design Services
http://newtonexcelbach.wordpress.com/
RE: AS3600 - Column or wall??
To compare wouldn't the M1/M2 be 0 as I would assume the wall is designed without bending moment? doing this would allow you to increase the le/r possibly?
http://www.nceng.com.au/
"Programming today is a race between software engineers striving to build bigger and better idiot-proof programs, and the Universe trying to produce bigger and better idiots. So far, the Universe is winning."
RE: AS3600 - Column or wall??
No, the column provisions are quite specific that M1/M2 is -1 for minimum eccentricity.
Doug Jenkins
Interactive Design Services
http://newtonexcelbach.wordpress.com/
RE: AS3600 - Column or wall??
http://www.nceng.com.au/
"Programming today is a race between software engineers striving to build bigger and better idiot-proof programs, and the Universe trying to produce bigger and better idiots. So far, the Universe is winning."
RE: AS3600 - Column or wall??
But it doesn't make a huge difference. I have added a line to the graph with M1/M2 = 0.
Doug Jenkins
Interactive Design Services
http://newtonexcelbach.wordpress.com/
RE: AS3600 - Column or wall??
More details and download at:
http://newtonexcelbach.wordpress.com/2013/07/21/us...
I have regenerated asixth's chart using this function:
I get slightly higher stresses for Le/r, maybe because of 500 MPa steel, or possibly some other difference in assumptions.
Doug Jenkins
Interactive Design Services
http://newtonexcelbach.wordpress.com/