Dear All.
Attached disturbance recorder of reverse power trip, Comtrade format,
protective terminal Micom P345.
Diesel generator 17MW.
Du-fuel, in trip time was operated on gas with about 13-14MW load.
Setting P1< 3% 10sec with 3sec reset time
P2< 8% 1sec with 0.1sec reset time.
Trip was after 10sec, but P2< with 8% was started too ( I was changed setting now on the 0.3sec of reset delay ).
AVR Excitation is Basler DECS200.
Grid is very very weak and unstable.
According to grid data,on this time, tripped some other generation unit with 10MW production, tripped by some electrical protection.
I think it was out of step situation ( pole slip, 78 ), Im not believe in some real reverse power: diesel fault.
What is your opinion
Thank in advance
Slava