Can you run 4-20mA analog & 125VDC contact sensing circuits as shielded prs in same multipaired
Can you run 4-20mA analog & 125VDC contact sensing circuits as shielded prs in same multipaired
(OP)
I know the conventional design is to run digital signals in one cable, and analog signals in another cable. I question why this is so if the individual pairs are shielded?
In our particular case we have some signals we want to pick up from about 500' away and there is a cable with individually shielded twisted pairs already in place. These signals are either just contact sensing - no power or outputs, or 4-20mA. I suppose the concern is induction onto the 4-20mA from on/off....?
In our particular case we have some signals we want to pick up from about 500' away and there is a cable with individually shielded twisted pairs already in place. These signals are either just contact sensing - no power or outputs, or 4-20mA. I suppose the concern is induction onto the 4-20mA from on/off....?
RE: Can you run 4-20mA analog & 125VDC contact sensing circuits as shielded prs in same multipaired
If you don't care if the analog values hop around during switching of limit switches or whatever, then you could probably 'get away with it'.
Keith Cress
kcress - http://www.flaminsystems.com
RE: Can you run 4-20mA analog & 125VDC contact sensing circuits as shielded prs in same multipaired
Best approach is to put the 4-20 mA level stuff in a separate metallic conduit.
RE: Can you run 4-20mA analog & 125VDC contact sensing circuits as shielded prs in same multipaired
RE: Can you run 4-20mA analog & 125VDC contact sensing circuits as shielded prs in same multipaired