In my company we have programe which contain alot of tasks and question and we must do it, So these question is from my programmes, for the first question i have the answer but i want to make sure if its correct or not (really I'm not student)
***Explain possible causes for level gauges to give false readings and how this can be corrected.
Answer:-
Possible Causes
1- Choking of level troll legs (usually the lower leg) due to sediments/sludge.
(Corrected action is:- Servicing of level troll is required.)
2- Stuck up Float: Float may get stuck in the level troll due to hydrate formation, or solid deposits. ( Corrected action :- servicing of level troll is needed.)
3- Loss of Glycol in the Glycol pot, where used.
(Corrected action :- Refill the glycol pot.)
4- Leaks from the connections on level troll. This will affect DP type transmitter due to false DP reading, and hence the level reading