MEUSA said:
We're looking into upgrading our system. Can we use MV MCCs to feed transformers, or do feeders have to be switchgears? What is prefered and why? Also, can I have transformers feeding LV MCCs directly, and not have to go though a LV switchgear? Is the a specific size HP for LV motors before it's prefered to use a switchgear breaker? I appreciate any assistance on this!
As I interpret your question, you are referring to FEEDING transformers from this equipment, and you are asking if it is better to feed transformers with circuit breakers in MV Switchgear, as opposed to feeding them with "Transformer Feeder Units" in MV MCCs, is that correct?
The difference, for the most part, is nominal but it also depends on what you prefer in terms of "Switchgear". If you want draw out Metal-Clad switchgear, then you will not get those advantages using an MCC. Metal-Clad vs Metal Enclosed is a separate decision making process too tangential for this discussion, other than if you DO want Metal-Clad, then the rest is a moot point. This is, by the way, in reference to ANSI (North American) standards for Switchgear design. If you are not in North America, then IEC Switchgear offers less clear differentiations.
But if you are referring to IEC equipment or were thinking of using Metal-Enclosed ANSI switchgear, then the basic construction is very similar to an MV MCC anyway, so there is only the difference between circuit breakers and contactors to consider. I'm going to assume you would only be considering Vacuum Circuit Breakers (VCB) vs Vacuum Contactors (VC) in this discussion.
The general issue of consideration in that issue is one of application. VCBs are not designed to operate as often as VCs, but a VC needs to have energy on the control coil continuously (excluding latched contactors for simplicity here). So if you are planning on energizing and de-energizing these transformers once per day, I would not use a VCB. That however is typically not how transformers are fed, it is more common that it is energized and left that way indefinitely. That makes a better case for feeding them from a VCB. But in a recent discussion I had with one of our PEs who does Arc Flash mitigation, he brought up an interesting point. If you are looking to use a Protection Relay system to lower your Incident Energy in the down stream equipment, a VC can actually operate faster than a VCB, because there is no mechanical unlatch time involved. I'm not deeply cognizant of all the issues with this because I just heard it mentioned for the first time very recently. But it's apparently something worth considering if this has any connection to Arc Flash mitigation.
From a protection standpoint, if you are going to specify a good Feeder Protection Relay anyway (or a similar level of high-end trip unit in a VCB) there is no reason to consider those issues between the two choices. If you were to want to use the less functional basic trip elements in a VCB, but were willing to allow only fuses in the MCC transformer feeder, then the MCC version is likely to cost you less. I can't recommend that though.