Level control in a horizontal cylindrical tank

Level control in a horizontal cylindrical tank

Level control in a horizontal cylindrical tank

(OP)
L.S.,

I would like to check a certain feature with others about copntrolling a level in a horizontal cylindrical tank. I have been taught that for level control it is wise to have a certain dead zone around the nominally desired level, so that small deviations will not immediately require controlling action and that the tank will function more like a volume buffer.
Are there any considerations pro or against to actually stick to this rule?

Thanking you in advance for your comment I remain

with best regards,

Karel Postulart

Karel Postulart, The Netherlands
Nuon Power Generation

RE: Level control in a horizontal cylindrical tank

The reason for the dead band is to minimize cycling of the valve [on-off].

RE: Level control in a horizontal cylindrical tank

(OP)
xnuke and sreid,

Thank you for your swift response and helpfull information.

With best regards,

Karel Postulart, The Netherlands
Nuon Power Generation

RE: Level control in a horizontal cylindrical tank

In support of;
"It depends..."
As an example of a dead band, we had a condensate return tank where the dead band was between about 15% and 20% of tank capacity. When the condensate return flow surged, the tank would go to almost 100%.
The normal operating level was between 20% and 90%. If the level went below 15% it was topped up to 20%. Not all of the steam was returned as condensate. From time to time, generally due to operator error, the level would go to 100% and excess water would overflow and be wasted.  

Bill
--------------------
"Why not the best?"
Jimmy Carter

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close