Level control in a horizontal cylindrical tank
Yobbo
NL
L.S.,
I would like to check a certain feature with others about copntrolling a level in a horizontal cylindrical tank. I have been taught that for level control it is wise to have a certain dead zone around the nominally desired level, so that small deviations will not immediately require controlling action and that the tank will function more like a volume buffer.
Are there any considerations pro or against to actually stick to this rule?
Thanking you in advance for your comment I remain
with best regards,
Karel Postulart
Karel Postulart, The Netherlands
Nuon Power Generation
It depends on the function of the tank. See
xnuke
"Live and act within the limit of your knowledge and keep expanding it to the limit of your life." Ayn Rand, Atlas Shrugged.
The reason for the dead band is to minimize cycling of the valve [on-off].
xnuke and sreid,
Thank you for your swift response and helpfull information.
With best regards,
In support of;
"It depends..."
As an example of a dead band, we had a condensate return tank where the dead band was between about 15% and 20% of tank capacity. When the condensate return flow surged, the tank would go to almost 100%.
The normal operating level was between 20% and 90%. If the level went below 15% it was topped up to 20%. Not all of the steam was returned as condensate. From time to time, generally due to operator error, the level would go to 100% and excess water would overflow and be wasted.
Bill
"Why not the best?"
Jimmy Carter