Generator field saturation

Generator field saturation

Generator field saturation

(OP)
If a generator field saturates power output decreases this at the same time  increases steam flow to turbine without changing steam pressure profile in turbine. i would like to know in detail , what would be the quantity of power loss and how to calculate it. please give in detail how to calculate power consumption due to field.

RE: Generator field saturation

Pstatorwinding=Ms x Rs x |Is|**2 Loss of Stator Power in watts
where
|Is|=(Xms x Ns' x Ef)/[(XLs + Xms) x Rf] is stator current in Amps
Ef rotor field voltage in Volts
Rf rotor field resistance in Ohms
XLs is stator leakage reactance << Xms in Ohms
Xms is stator magnetizing reactance in Ohms
Ns' = 3 x Nr/(sqrt2 x Ms x Ns)
Ms is number of stator phases
Nr number of rotor turns
Ns number of stator turns

RE: Generator field saturation

hey S, I think you got things mixed up.

the dc field in a syn. gen. does not "saturate", however the ac core saturates and this limits the voltage induced in the armature winding by the field.

Second, changing excitation (magnetization) levels in a synch. generator changes Var generation not Power generation.  Only the steam turbine governor can change Power output of the generator.

Now changing Vars loading will change the losses in the generator(stator core loss, armature loss, stray load loss) but these losses are small compared to the power output in any well designed generator.

RE: Generator field saturation

It will not reduce the out put.THe change in the field excitation is only conncted to the reactive power.There by only the voltage will change if it is running in solo or the power factor will change if it is running in paralell.The active power will not get changed and it is enterly depends on the steam flow and the governertrottling if it is in parallel with grid or another gen.Or the amount of load it is impoed on.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close