Convert corner ground delta service to 3 phase ungrounded delta servic

Convert corner ground delta service to 3 phase ungrounded delta servic

Convert corner ground delta service to 3 phase ungrounded delta servic

(OP)
The existing old 600 amp, 240V 3 phase service is corner grounded delta. The main fusible service panelboard is rated for 1 phase (with two bus-verified after opening the switchboard). All the HVAC loads fed from this panel are 3 phase loads fed from 1 phase rated switchboard. This installation is not code compliant and now there is some proposed HVAC renovation work.

So, when I specify a new 3 phase service entrance rated switchboard, I am  not sure whether to leave the service as corner ground delta or change it to 3 phase ungrounded delta.

Converting this to 3 phase 4 wire would be ideal but the owner doesn't have budget for that.

This is a bank building so there is no maintenance on-site.
Any suggestions; corner ground delta or ungrounded delta?
Replies continue below

Recommended for you

RE: Convert corner ground delta service to 3 phase ungrounded delta servic

Forget both. Use a four wire, center grounded delta. That will give you 240V Volt three phase, 120/240 Volt single phase and a good safe grounding system.
Use a three phase panel and one extra wire from the center tap of one of the 120/240 volt transformers.

Bill
--------------------
"Why not the best?"
Jimmy Carter

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close