Genset building classification
Genset building classification
(OP)
a. What is the occupancy classification for a CMU building housing a diesel generator set ("genset") with a 500 to 900 gallon belly tank (double wall)? IBC 2009. I'm leaning toward U (Utility and Misc).
b. Is 2-hour fire rating required?
c. Is fire suppression required?
d. Is there an NFPA code more applicable, or make more requirements, than IBC?
The building is small CMU (14' x 20') with wood framed roof and one layer of 5/8" gypboard. Double doors one end. Adjacent structure is 10 feet away. Site is unoccupied wastewater pump station.
b. Is 2-hour fire rating required?
c. Is fire suppression required?
d. Is there an NFPA code more applicable, or make more requirements, than IBC?
The building is small CMU (14' x 20') with wood framed roof and one layer of 5/8" gypboard. Double doors one end. Adjacent structure is 10 feet away. Site is unoccupied wastewater pump station.
RE: Genset building classification
B. Unable to answer. What's the location of the generator in relation to the property line?
C. No
D. Depends on what codes and standards are adopted in the jurisdiction
RE: Genset building classification
Thanks for the reply.
b. Not near a property line.
Variation on question c. There is a second, almost identical structure where roof is simple 2x wood framing (not pre-engineered trusses) with no ceiling or gypboard protection - just exposed wood.
Seems like at least a one-hour ceiling is required, considering both the diesel fuel and the generator. Does the IBC address this?