There is a code you’re looking for is, “Standard Practice for Bracing Masonry Walls under Construction.” (BMW)
When you’re constructing CMU walls over 8’, wind becomes a factor as stated previously. A masonry block wall can be constructed up to 8’ in winds up to 35mph winds during the initial period. The initial period in the first working day and the intermediate period is any time after the first working day until all structural elements are in place as designed. Say you were constructing a 21’ wall, 8” 125psf CMU’s w/ S type mortar. From BMW, T4.2, the max height is 14’ for the initial period, by the end of the day a brace would need to be placed at a height 11’-4,” BMW TA1. This table also states that the max unbraced height is 5’-4,” 14’-11’-4” = 2’-8”, less than max. ok. The remainder of the wall could be built the next day. There also needs to be a restricted zone that must be evacuated when the winds exceed 35mph.
To answer your last question, a Masonry Contractor w/ some substantial experience could use the BMW. If it’s not stated in the subs contract the they need to have a bracing plan, that it’s up to the GC to provide a safe work zone for all that enter the site.