Source Impedance Ratio (SIR) Calculation

Source Impedance Ratio (SIR) Calculation

Source Impedance Ratio (SIR) Calculation

(OP)
I would like to get opinions when calculating Source Impedance Ratio (SIR) on a Power System.

Usually I have seen a three Phase fault** and only taken into account the positive sequence components of the Source and divide this by the positive sequence component of the protected line.

Also, I have seen calculating a single line to ground fault**, and taken all the sequence components of the source and add them together, and divide this by the SUM of the positive, negative and Zero sequence impendances of the line being evaluated.

**The fault is at the terminal were the relay is being evaluated, and the fault does not consider the line in service so that the Thevelin equivalent impedance with the voltage source is only from the System.


Now, I see that performing a single line to ground fault and breaking down into sequence components and getting the SIR for that, is very different that for a three phase fault that only have positive sequence components.

My QUESTION is: Is there a benefit or assumption that would justify to calculate the SIR only on based only on Positive sequence components ??? since I consider is ignoring things/effects like grounded impedance, mutual couplings, etc.

Thanks,

Luichip

RE: Source Impedance Ratio (SIR) Calculation

The new specification IEC 60255 for line distance protection will define SIR. For phase-ground faults you need, to my opinion, to consider also the earth-return impedance, which is function of positive sequence impedance and zero sequence impedance. It is common to assume negative sequence impedance = positive sequence impedance. You will also see that by simply putting the three sequence components circuits in series.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close