The VFD cable has a following voltage ratings: 600V (UL type TC-ER) and 1000V (UL type motor supply). Do these ratings mean that the cable insulation is designed to operate at 1000V RMS, but is limited to 600V RMS when used in cable tray/exposed run application?
Another issue: as per MG-1, Part 31 the inverter duty motor insulation should withstand 3 times of line-to-line RMS voltage due to possible voltage build-up at motor terminals. Should the motor cable selection be based on the fact that the cable insulation is stressed the same way as the motor insulation? For 480V motor the above mentioned cable rating 1000V might be insufficient, and 2000V cable should be used. Is this a correct approach?
Another issue: as per MG-1, Part 31 the inverter duty motor insulation should withstand 3 times of line-to-line RMS voltage due to possible voltage build-up at motor terminals. Should the motor cable selection be based on the fact that the cable insulation is stressed the same way as the motor insulation? For 480V motor the above mentioned cable rating 1000V might be insufficient, and 2000V cable should be used. Is this a correct approach?