VFD partial load efficiencies
VFD partial load efficiencies
VFD Efficiency at
VFD | % Full Load
HP | 25 33 50 66 75 100
------|----------------------------------------------
1 | 0.12 0.28 0.52 0.68 0.75 0.92
2.5 | 0.21 0.36 0.58 0.73 0.79 0.93
5 | 0.27 0.42 0.63 0.76 0.82 0.94
10 | 0.33 0.48 0.67 0.80 0.85 0.96
25 | 0.42 0.55 0.74 0.84 0.89 0.97
50 | 0.48 0.61 0.78 0.88 0.92 0.98
100 | 0.55 0.67 0.83 0.91 0.95 0.99
250 | 0.63 0.75 0.89 0.96 0.98 1.01
Is the % Load of the VFD calculated as,
VFD%Load = Motor Load / Motor Nameplate Rated Power?
Like this,
Motor Rated Power = 100 HP
Load = 50 HP
Motor Reduced Load = 50%
Motor Reduced Load Eff = 0.89
Motor Brake Power = 50/0.89 = 56.2 HP (41.9 kW)
VFD Rated Power = 75 kW
VFD Load% = 41.9/75 = 55.8 %
100 HP VFD eff = (50%,0.83) (66%, 0.91)
giving a VFD Eff = 83 + (55.8-50)*(0.91-0.83)/(66-55)*100
VFDreduced eff = 87.2%
So,
Line Power = 41.9 kW / 0.872 = 48 kW
Right?
Thanks
"We have a leadership style that is too directive and doesn't listen sufficiently well. The top of the organisation doesn't listen sufficiently to what the bottom is saying." Tony Hayward CEO, BP
**********************
"Being GREEN isn't easy" ..Kermit
http://www.youtube.com/watch?v=hpiIWMWWVco
http://vir
RE: VFD partial load efficiencies
But then they imply that same VFD drops down to being only 12% efficient at 25% speed? What kind of VFD did they use to come up with that kind of horrific value?
That leads me to believe that their use of the term "VFD Efficiency" is not what I think of it as being.
"If I had eight hours to chop down a tree, I'd spend six sharpening my axe." -- Abraham Lincoln
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies
RE: VFD partial load efficiencies
Uh, and the question?
"We have a leadership style that is too directive and doesn't listen sufficiently well. The top of the organisation doesn't listen sufficiently to what the bottom is saying." Tony Hayward CEO, BP
**********************
"Being GREEN isn't easy" ..Kermit
http://www.youtube.com/watch?v=hpiIWMWWVco
http://vir
RE: VFD partial load efficiencies
This one does have better values.
http://
"We have a leadership style that is too directive and doesn't listen sufficiently well. The top of the organisation doesn't listen sufficiently to what the bottom is saying." Tony Hayward CEO, BP
**********************
"Being GREEN isn't easy" ..Kermit
http://www.youtube.com/watch?v=hpiIWMWWVco
http://vir
RE: VFD partial load efficiencies
But yes, if you know the VFD efficiency, the input kW would be computed as you suggest.
David Castor
www.cvoes.com
RE: VFD partial load efficiencies
Yes I thought the 101 was a bit strange.
The new chart looks more reasonable in all aspects.
Thanks to both for the help.
"We have a leadership style that is too directive and doesn't listen sufficiently well. The top of the organisation doesn't listen sufficiently to what the bottom is saying." Tony Hayward CEO, BP
**********************
"Being GREEN isn't easy" ..Kermit
http://www.youtube.com/watch?v=hpiIWMWWVco
http://vir
RE: VFD partial load efficiencies
I like the information in your 2nd link a lot better, that's more of what I would expect to see. It looks to be a well thought out study. Thanks for that by the way, it may come in useful to me too.
Just out of nosy curiosity, what is the purpose behind you gathering this info? Are you evaluating the efficacy of an energy saving VFD installation?
"If I had eight hours to chop down a tree, I'd spend six sharpening my axe." -- Abraham Lincoln
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies
RE: VFD partial load efficiencies
"We have a leadership style that is too directive and doesn't listen sufficiently well. The top of the organisation doesn't listen sufficiently to what the bottom is saying." Tony Hayward CEO, BP
**********************
"Being GREEN isn't easy" ..Kermit
http://www.youtube.com/watch?v=hpiIWMWWVco
http://vir
RE: VFD partial load efficiencies
There is a new standard trying to get out into the big wide world that covers, amongst other things, VFD efficiency. It is owned by the organisation AHRI (Air-Conditioning, Heating, and Refrigeration Institute) and will be known as "Standard 1210, Performance Rating of Variable Frequency Drives". The intention is that this standard will be used by consultants and institutes who are looking to advise their clients and contractors alike regarding performance of the VFD's used on Green Buildings to ensure that complying with higher level of performance in the building is in line with the products being supplied.
It is taking forever to be released but when it is, I feel it will be suitable for many other industries looking at the products and their performance. Hopefully it will provide clarity and demystify certain thoughts such as "all VFD's are the same...".
It will also include factors such as recommended limits of harmonic (current) distortion levels from the product, stresses on the motor insulation as a result of PWM waveform etc.
At the moment it is still in draft form and not released. When it's released I will try and remember to advise the forum
RE: VFD partial load efficiencies
Looking at the paper for a VFD, it appears that there is about 3-4% extra losses at full speed and load and the losses increase to about 6% to 7% as the speed reduces to 75% speed. The relative efficiencies track with load fairly well so the load doesn't really matter. So, a system with a valve with less than about 4% to 5% losses would compete very well with a VFD.
RE: VFD partial load efficiencies
"We have a leadership style that is too directive and doesn't listen sufficiently well. The top of the organisation doesn't listen sufficiently to what the bottom is saying." Tony Hayward CEO, BP
**********************
"Being GREEN isn't easy" ..Kermit
http://www.youtube.com/watch?v=hpiIWMWWVco
http://vir
RE: VFD partial load efficiencies
The VFD adds about 3% extra losses (motor + VFD) best case and it increases from there. In the common range where a pump or fan would operate the extra losses appear to increase to around 6% or 7%. This is assuming the typical range would be around 70% speed to 100% speed.
One other thing to consider is that paper did not include any type of harmonic mitigation or vfd to motor filtering. Typically, you'll see at least one line reactor in the package. As a general rule of thumb you could assume 2 reactors (input and output) will double the VFD package losses. More complex filters will add even more losses.
Sure, you don't want to lower the speed of a motor if the process allows for more revenue producing output at full speed but you may have to lower the speed of the motor if the process itself requires less output.
RE: VFD partial load efficiencies
That filter effect on power is quite interesting. I wasn't aware of that effect. By doubling the "VFD package" losses, do you mean multiply the VFD partial load efficiency values in the table by 2? And how would addtional filters affect that factor?
BTW, I'm trying to develop an equation to duplicate the VFD partial load efficiencies in that table. Its hard to come up with something that is within 1 or 2 percent of all those values, even if you ignore the lowest power ratios and the 1 HP motor. If anyone comes up with one, its good for a virtual beer.
"We have a leadership style that is too directive and doesn't listen sufficiently well. The top of the organisation doesn't listen sufficiently to what the bottom is saying." Tony Hayward CEO, BP
**********************
"Being GREEN isn't easy" ..Kermit
http://www.youtube.com/watch?v=hpiIWMWWVco
http://vir
RE: VFD partial load efficiencies
RE: VFD partial load efficiencies
"We have a leadership style that is too directive and doesn't listen sufficiently well. The top of the organisation doesn't listen sufficiently to what the bottom is saying." Tony Hayward CEO, BP
**********************
"Being GREEN isn't easy" ..Kermit
http://www.youtube.com/watch?v=hpiIWMWWVco
http://vir