UL bus rating vs overcurrent device
UL bus rating vs overcurrent device
(OP)
This just doesn't seem right to me and wanted to see what others think. We use a product (DC fuse panel) with a bus rating of 100A. Per UL we need to protect it with a max. 125A overcurrent device. However they only thermal test that product to the bus rating of 100A. With a 125A overcurrent device that product could hum along for ever at 125A without the overcurrent device ever tripping.
I would think that you should protect it with an overcurrent device no greater than your bus rating. So bus rating = 100A, overcurrent device = 100A. Is this yet another hole in the standards that hasn't been plugged?
I would think that you should protect it with an overcurrent device no greater than your bus rating. So bus rating = 100A, overcurrent device = 100A. Is this yet another hole in the standards that hasn't been plugged?
RE: UL bus rating vs overcurrent device
DW
RE: UL bus rating vs overcurrent device
I have a feeling this is just incorrect and that it should be a 100A bus rating, a 100A interupt device with the wiring sized to 125A.
RE: UL bus rating vs overcurrent device
RE: UL bus rating vs overcurrent device
Could it be that there's an allowance for loads that have inrush current (capacitive things I guess)? Same way we protect motor circuit conductors with overcurrent protection set higher than listed ampacity.
I can see how that might be needed. Each circuit coming off your bus has its own fuse protection, so if properly designed it might be OK.
Personally, I'd put a 100% protector on it (or less, depending on my loads)... The 125% is a maximum after all.
Anyway, I'm just thinking while typing --
Anybody else out there?
Good on ya,
Goober Dave
RE: UL bus rating vs overcurrent device
It just doesn't seem right.
RE: UL bus rating vs overcurrent device
RE: UL bus rating vs overcurrent device
You have to remember that UL comes in thinking about fire safety 1st and above all other concerns. Electrical safety, while important is a second class citizen. I've worked with UL on products under UL 1778, 60950, & 508A and it's always the same. I belive if you check the NEC standards (again a fire safety standard), you'll see the 125% is pretty common.
Steve Smith
RE: UL bus rating vs overcurrent device
You should see the tests they do for small transformers, it's a hoot.
Goober Dave
RE: UL bus rating vs overcurrent device
No thanks on the transformer test. I've had my fill with UPS, Power Factor Correction equipment, & UL 924 Emergeny Power Systems.
Steve Smith
RE: UL bus rating vs overcurrent device
Thanks guys...
RE: UL bus rating vs overcurrent device
So your 100 A bus is now only good for 80 A on a continuous basis.
David Castor
www.cvoes.com
RE: UL bus rating vs overcurrent device