That was Alan's link, not mine Rafiq.
With identical machines, the harmonics will be identical. With identical harmonic profiles in parallel no current will circulate. Circulating currents are the result of dissimilarities between the generators.
You first must determine the actual difference between supposedly identical machines.
If practice it may be easier to just measure the circulating currents.
I know we are supposed to anticipate and calculate everything in advance, but that is not always possible.
What is possible is to spec the maximum allowable differences in harmonic production and to then test and verify that these conditions have been met during acceptance tests.
Remember, although harmonic currents may flow to the load through the neutral, the circulating currents on the ground loop are dependent on the differences between the harmonic production of the generators.
Bill
--------------------
"Why not the best?"
Jimmy Carter