One way Shear check in circular footing?

One way Shear check in circular footing?

One way Shear check in circular footing?

(OP)
How The one way shear can be checked in circular footings,(not punching),,,Eargent answer needed plz...
Replies continue below

Recommended for you

RE: One way Shear check in circular footing?

Doing exactly in the same manner that with rectangular footings should be safe enough, counting with the loads really acting (segment of a circle). More conservative of course would be dimensioning for the maximum cantilever in the direction.

If you want more exact values you can model the footing with thick plates or even solid brick elements and see what happens, both overkill.

RE: One way Shear check in circular footing?

(OP)
I need to know the segment you mentioned,is circular or ... tangent to a circle with D distance of the circular column on it?

RE: One way Shear check in circular footing?

A segment, that is a sector minus the included triangle.

I don't find any example in a book, but all say at d of face, hence at above.

If your application is critical better do a detailed analysis, then you may average a bit the stresses along any plane you consider.

Really I never practice footings where shear controls so if too adjusted to the strength I would likely proceed the FEM way.

RE: One way Shear check in circular footing?

I would proceed as ISHVAAAG has outlined in defining the critical section (distance 'd') away from the column.  If the column is round use the equivalent square to determine where 'd' must be measured from.  Use the segment of the cirle outside of this critical section to determine the shear.  This will be conservative for all locations or variations.

If there are problems, then increase the footing thickness.  Concrete is cheap compared to design time and worry.

I would not, employ a FEM as it would take entirely too long to develop (even in a commercial package) for what amounts to an approximation which is what we're doing via the aforementioned analysis.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close