I've done lots of conc beams spanning 59' to 60' for parkades and they have a pile of reinforcing... Typical Geometry beams spaced at 15' centres with 5-1/2" conc slab over. T-beams are 36" deep x 16"-18" wide stem and design loads are 50 psf LL for parking loading. They are typically part of a multi-storey frame with horizontal members at 10' spacing. The columns are roughly 16" x 36"(perp to span) with reinf approaching max.
In the beams, you have to check for flexure and shear (both can be high) as well as deflection, cracking, vibration wasn't an issue. You also have to check for rebar placing because of congestion of bars at the columns. Beam to column fixity assumed to be monolythic and spread footing assumed to be rigid at base (good granular material). Effective EI for columns calculated taking into effect of crackingas well as stress level of concrete. Maximum reinforcing occurred at upper most column due to lack of vertical load.
Other than that, nothing out of the ordinary.
Dik