monitoring gas usage on large cure ovens

monitoring gas usage on large cure ovens

monitoring gas usage on large cure ovens

(OP)
Hello,
  I looking for an average to mid-range gas meter that can be mounted in line on a burner control to monitor gas useage. We are attempting to make changes to our oven controls and we would like to observe maybe document (record) the before and after effects of our efforts. Our main line preasure is 30 psi and the burners are manufactured by Maxon first is 2.5 million BTU and is  2 pipe with 5 psi of natural gas. The other is a Maxon burner 3.5 million BTU 2 inch pipe. Each of these units are in different location. Please forgive me if this isn't in the correct forum. Any suggestion will be appreciated.

2571
Replies continue below

Recommended for you

RE: monitoring gas usage on large cure ovens

If your consumption is sufficiently high you may also add T&P correction.
Suggest you try an internet search for them but you could start with Actaris;
http://www.actaris.com/html/eng/GAS/3-15.html
For your needs perhaps the MZ quanticometer which is a turbine type and low cost.

JMW
www.ViscoAnalyser.com

RE: monitoring gas usage on large cure ovens

Watch about putting. a meters on ovens as the cost of meter and installation will eat up any saving for a year or two. Case in point we had a pyrolysis furnace that had a total burner capacity of 900,000 BTUS'.  Accounting insisted that we install a gas meter for charges. The end result was that we could have run the furnace 24/7/365 for over two years for the installed cost of the meter.

Check with your gas supplier they may have a loner or rental unit.   

Here are the meter we use
http://www.americanmeter.com/en/index.shtml

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close