Generator Sizing

Generator Sizing

Generator Sizing

(OP)
Dears,

I am going to size a generator for a MCC of 350KW max demand.Can some one provide any procedure/code of practice to calculate the generator size



 

RE: Generator Sizing

I suggest you discuss your application with your likely generator suppliers.  They will be happy to discuss sizing criteria.  Many have software for calculating necessary generator size based on your specific load profile.

One important factor will the largest motor that you will be starting and its inrush current.  Also, what level of voltage drop can you live with on motor starting.  

dpc

RE: Generator Sizing

I have touched various manufacturrers, but didn,t find any comprehensive calculation method. Cosidering Maximum demand, Starting currents, diversity and spare reconsiderations. IF any one have some literature then please send me

RE: Generator Sizing

Here is a basic rule of thumb for generator sizing based on motor starting.  The generator should have spare capacity available of twice the size of the motor in order to start it.  

For example, a 400 kVA genset can start a 200 kW motor.  Once the motor is running, only 200 kVA is spare, so a 100 kW motor is the largest motor that can then be started.  If you started the 100 kW motor, you would not be able to start the 200 kW afterwards as there is only 300 kVA spare. Rough, but it works.  

What is important though is to properly sequence motor starting.  Where possible, get the big motors away first.

RE: Generator Sizing

Consideration about diversity and spare availability?

I think diversity for MCC,s is 0,6 of MAX. Demand and spare capacity is 1.2

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

White Paper - Implementing a Multi-Domain System
IoT systems are multi-domain designs that often require AMS, Digital, RF, photonics and MEMS elements within the system. Tanner EDA provides an integrated, top-down design flow for IoT design that supports all these design domains. Learn more about key solutions that the Tanner design flow offers for successful IoT system design and verification. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close