High-tertiary impedance design change from 12% to 26%

High-tertiary impedance design change from 12% to 26%

High-tertiary impedance design change from 12% to 26%

(OP)
Can somebody explain what would be the effect of changing the H-Y (high to tertiary) impedance in a 120/160/200 MVA, 260-144/25 kV, three phase  autotransformer, from 12% (required) to 26% (per design). The H-X impedance is 5%.
Thanks for the info.

RE: High-tertiary impedance design change from 12% to 26%

The question is not clear.Can you explain?What is meant by "required" and "designed"?Also indicate T-X impedance also on both cases.Hope H-Ximpedance remains the same.

RE: High-tertiary impedance design change from 12% to 26%

(OP)
A corp. requires a 120/160/200 MVA auto Xfr with H-X=5% and H-Y=21% requirements. However our engineering can only comply with the H-X at 5%, and only provide H-Y = 36% impedance instead of 21%. My questions is what can possibly change with our  deviation? Does it matter if the tertiary is buried or if it is loaded? If so, why should that be?

RE: High-tertiary impedance design change from 12% to 26%

If the tertiary is buried it will not matter at all ,but in a way better as the circulating current in tertiary will be reduced.But if it is aloaded tertiary ,regulation at tertiary terminals  will be higher as the T arm of the circuit will have higher impedance.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close