Relay & Energy consumption
Relay & Energy consumption
(OP)
Hi guys.
As we know, if a DC current applied into a coil, enery will be needed to build up the magnetic feild surrounding the coil, once that is done there will be no energy needed and no energy consumption (neglect the coil resistance )- I hope I am right.
Now in case of a relay coil operates against its spring to pull up its contacts and keep them closed, there will be energy needed to operate aginst the spring while the contacts are moving to the close position.
My question now, what will be the situation after the contacts closed - Is any anergy is needed to keep the contacts closed against the spring ?
Thanks in advance
As we know, if a DC current applied into a coil, enery will be needed to build up the magnetic feild surrounding the coil, once that is done there will be no energy needed and no energy consumption (neglect the coil resistance )- I hope I am right.
Now in case of a relay coil operates against its spring to pull up its contacts and keep them closed, there will be energy needed to operate aginst the spring while the contacts are moving to the close position.
My question now, what will be the situation after the contacts closed - Is any anergy is needed to keep the contacts closed against the spring ?
Thanks in advance
RE: Relay & Energy consumption
Although you are not changing the energy in the magnetic field (as you correctly assume in your first paragraph) or in the spring, you are having to supply the heat losses due to coil resistance. All you can do is reduce the coil current to a level that just holds the contacts closed.
RE: Relay & Energy consumption
On the electrical side, voltage would equal zero in the theoretical steady state dc system with all resistance =0. electrical power = voltage times current = 0 times current = 0.
On the mechanical side:
mechanical power = force times velocity = force times 0 = 0
since velocity = 0 once the coil is pulled in.
velocity = 0 once the coil is pulled in so
=====================================
Eng-tips forums: The best place on the web for engineering discussions.
RE: Relay & Energy consumption
energy cosumption after that ( if the coil resistace is neglected}.
But at the same time we have to pass enough current through the coil to get the magnetic field required to produce pulling force equal to or greater than the opposing
spring force.
Now, if we know the value of the force of the the spring
When the cotacts are fully closed, whow we can calculate
the minimum current required to keep the contacts closed ?
RE: Relay & Energy consumption
http://www.webspawner.com/users/israelkk/
RE: Relay & Energy consumption
RE: Relay & Energy consumption
Thanks
RE: Relay & Energy consumption
RE: Relay & Energy consumption
RE: Relay & Energy consumption
F = B2A / 2μ0
(all in SI units; A is the pole face area, B is flux density, μ0 is permeability of free space)
Strictly speaking this is the force between two facing poles separated by an airgap, applicable provided the airgap isn't large compared with the pole face diameter or width (otherwise you will have difficulty deciding what value of B to use).
I'm not sure what your magnetic circuit looks like; if when your "contacts" close the airgap in your magnetic circuit also closes, then just assume a very small airgap still exists (experiment by decreasing the value of airgap until you arrive at a maximum value of B) and calculate the total reluctance of the magnetic circuit. Then find how many ampere-turns you need to match the spring force when the contacts are closed.
RE: Relay & Energy consumption