I am looking for a reference or a procedure to determine the allowable bending stress for laterally unbrased steel tubes and pipis sections. (particularly for Kl/r's up to 200).
Replies continue below

Recommended for you

RE: Allowable Bending Stress for Unbrased Tubes and Pipes

Are you in the U.S.?  Check on AISC Specifications or British standards depending on your location.

RE: Allowable Bending Stress for Unbrased Tubes and Pipes

(OP)
I am in the US. I seem to remembered reading that the plactic moment will be reached before any buckling occurs in closed sections such as tubes and pipe, thus no addition reduction in the allowable bending stess would be required. Any thoughts?

RE: Allowable Bending Stress for Unbrased Tubes and Pipes

You may find the specific procedure in LRFD appendix F where it is seen the unbraced length does not count. A circular pipe simply can't have what is called lateral buckling, lateral kink only develops as a consequence of local buckling; hence the determining factor is the local slenderness Diameter to thickness ratio that rules local buckling.

Whenever the Diameter to the thickness ratio is lesser than

2070/Fy

where Fy is to the number of ksi of yield strength of the steel, you can use the plastic capacity of the ring affected by the material strength reduction factor as the limit strength to compare with moments coming from factored forces of LRFD.

ASD for allowable stress design (service level design) is even simpler; if D/t is lesser than 3300/Fy, use 0.66·Fy as the Allowable strength to be compared with forces coming from the service level loadcases mandated in ASD.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close