steel joist damage

steel joist damage

steel joist damage

(OP)
Does any body know of any resources for evaluating damage to open web steel joist (bar joist)? I am evaluating one that got hit perpendicular to the bottom chord with a highlift. The bottom web was displaced so much it crippled the cross bracing. The bottom flange came back to about 1' displacement from the plane of the web. But I need to research how much this may have lowered the tensial capacity of the bottom chord. My original thoughts are to obviously replace any damaged cross bracing and bolt a steel plate to the bottom chord to repair the tensial strength of the damaged area. The top chord and web members appear undamaged. If anyone has any thoughts I would appreciate it. Thanks
Replies continue below

Recommended for you

RE: steel joist damage

With that much deformation, you need to check ALL weld connections as they might have been cracked.  Check the connections of the joist bearing and the connections in the joist itself.  Since the bottom chord had been plastically deformed, you should consider replacing.  If impractical to replace, do significant strengthening to correct the deficiency.  Make sure the joist is pulled back into place and is plumb.  Remove all sweep and restore lateral bracing.

RE: steel joist damage

(OP)
Thanks for the suggestions. We are planning on bolting plate to the  bottom chord to restore tensial strength and are scheduling a lift to examine all the welds and connections and label the members so the repair crews know what to do to what member. Thanks again

RE: steel joist damage

I strongly suggest replacing the joist. It sounds damaged beyond the point where it is repairable.

You can specify a new joist with either a splice at mid-span or one bearing end left off to be added on in the field. This will allow enough room for the erector put it up. A fabricator can combine this order for one joist with another job.

Make sure that the joist supplier designs this new joist as laterally unsupported between bridging lines or provide a special detail to continuously laterally brace the joist against the deck.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close