It looks like there is an error in the SLD. Per the dwg given, you have connected a 150kVA, Zig Zag transformer
with a primary voltage of 33kV to your 400V DELTA system which is the output of 30MVA, 132-0.4kV main transformer?
How it could be?

 
150MVA, ZNyn11 Interconnected Star-Star Transformer
Is the zig-zag winding phase/phase voltage 400V ?
Is the star winding phase/phase voltage 132 kV ?
Are both star points solidly earthed ?
 