Referring to a single line diagram, I'd like to confirm the size of the Zero sequence current transfromer.
Full load amps for this 4.16kV motor is about 800A. In addtion to 1600:5 CT(3), motor protection relay has a set of zero sequence CTs .
Zero sequence current transforer (a set with single CT for all phases) is rated 50:5. I am trying to confirm the size of this CT, i.e. 50:5. My assumption is that the reason for this CT size is due to the transformer feeding this 4.16kV bus that feeds the motor. The transformer is resistor grounded at 25A 10sec. Is this correct?
Full load amps for this 4.16kV motor is about 800A. In addtion to 1600:5 CT(3), motor protection relay has a set of zero sequence CTs .
Zero sequence current transforer (a set with single CT for all phases) is rated 50:5. I am trying to confirm the size of this CT, i.e. 50:5. My assumption is that the reason for this CT size is due to the transformer feeding this 4.16kV bus that feeds the motor. The transformer is resistor grounded at 25A 10sec. Is this correct?