I have reports from a site I'm involved with regarding unwanted current flow in a generator neutral.
The generator is a solidly grounded 2000 kW/2500 kVA wye connected diesel unit, directly feeding a 2500 kVA step up transformer at 480 volts. The transformer is 480 volts delta (secondary - connected to generator) to 12.5 kV wye (primary - connected to system with a resistance grounded primary).
No current flows until the 480 volt generator breaker is closed, conecting the generator to the transformer, at which time we see about 30 amps flowing on a generator (there are 12 units parallelled at the 12.5 kV level and all exhibit similar behavior, except one which has about 80 amps flowing). The current was measured with a clamp on ammeter directly in the generator neutral.
The ground fault relay trips when this occurs.
I recommended to my clinet that we look at the harmonic current content of the neutral current. - The 3rd harmonic current will look like zero sequence.
Here's my question: If the delta connection traps the triplen harmonics, where's the return path to the generator neutral?? Any other ideas on where to look??
The generator is a solidly grounded 2000 kW/2500 kVA wye connected diesel unit, directly feeding a 2500 kVA step up transformer at 480 volts. The transformer is 480 volts delta (secondary - connected to generator) to 12.5 kV wye (primary - connected to system with a resistance grounded primary).
No current flows until the 480 volt generator breaker is closed, conecting the generator to the transformer, at which time we see about 30 amps flowing on a generator (there are 12 units parallelled at the 12.5 kV level and all exhibit similar behavior, except one which has about 80 amps flowing). The current was measured with a clamp on ammeter directly in the generator neutral.
The ground fault relay trips when this occurs.
I recommended to my clinet that we look at the harmonic current content of the neutral current. - The 3rd harmonic current will look like zero sequence.
Here's my question: If the delta connection traps the triplen harmonics, where's the return path to the generator neutral?? Any other ideas on where to look??