Suggestion to jghrist (Electrical) Sep 15, 2003 marked ///\\jbartos,
In the same edition of the Westinghouse T&D Book, Chapter 5, XXI.56, p. 138 says "The impedance to the flow of zero-sequence currents in three-phase core-form units is generally lower than the positive-sequence impedance."
///Yes, agree. However, the original posting calls for relationships. The relationship does not necessarily mean the equality.\\ This doesn't show up in Table 5 where, for instance, Connection A-1, Star/Star Solidly Grounded shows both Z1% and Z0% = Z45%.
///Agree.\\\
Stevenal is correct.
///Yes, for the three-leg core-form transformer. However, the original posting does not indicate a type of the transformer. Therefore, I use the very same page of the cited reference excerpt:
The impedance of a three-phase bank of two-winding transformer to the flow of zero-sequence currents is equal to the positive-sequence impedance for three-phase shell form units (or for a bank made up of three-single phase units) if the bank is star-star with both star points grounded.
If the bank is connected star-delta, with the star point grounded, the zero-sequence impedance viewed from the star-connected terminals for shell-form transformer units, or banks of three single-phase units, is equal to the positive-sequence impedance; the zero-sequence impedance viewed from the delta-connected terminals is infinite.
It is clearly seen what I have stated in my posting in terms of dependency on the transformer winding, grounding, etc. is correct.
The steneval posting indicates just a portion of the sought information in the original posting.\\\