Just a speculative question, why can we not get a YNd6 vector group transformer. Is it because of the limb design and winding process used in YNd type transformers.
 
Replies continue below

Recommended for you

Any Yd transformer always has an odd-numbered vector group because of the inherent 30º phase shift in the Yd (or Dy) connection. You could use an inter-star (zigzag) winding in lieu of the Y and get a ZNd6 transformer.
 
You can have Yd1,Yd5,Yd7&Yd11 connections also Yy6, Dd6 & Dz6.
 
You can have Yd1,Yd5,Yd7&Yd11 connections also Yy6, Dd6 & Dz6.
 