What a delightful drive! Very solid piece of work.
I have one running a 1/2hp motor. The motor drives a chain thru an air powered clutch/brake. Every time the clutch engages(every 3 seconds) the motor takes a hit that the VFD supports. The motor actually stalled each hit until I reset the drive from "Normal Application",(pumps and fans and their ilk), to "Heavy Duty",(conveyors etc). That sets limits in the drive from 130% excursions up to 150%. This stopped all stalling. I then changed from scalar to vector and let the drive tune the motor. Everything is working fine now.
However, now and then the chain can jam on the product carriers. It jams hard. This starts a spectacular chain of nasty events since the product is eggs. LOL
I'm planning on using one of the digital outputs to tell the PLC to abort when a jam occurs. This will prevent 150 eggs from being forced through out of position chains.
I've discovered this drive has a torque overload sensing ability that is gated by a user set time. If the torque exceeds a certain amount for longer than a certain time the drive will close a contact.
Does this drive actually know what the torque is?? Or is this really the same as the current?
Technical manual link for it: (15MB)
Keith Cress
kcress -
I have one running a 1/2hp motor. The motor drives a chain thru an air powered clutch/brake. Every time the clutch engages(every 3 seconds) the motor takes a hit that the VFD supports. The motor actually stalled each hit until I reset the drive from "Normal Application",(pumps and fans and their ilk), to "Heavy Duty",(conveyors etc). That sets limits in the drive from 130% excursions up to 150%. This stopped all stalling. I then changed from scalar to vector and let the drive tune the motor. Everything is working fine now.
However, now and then the chain can jam on the product carriers. It jams hard. This starts a spectacular chain of nasty events since the product is eggs. LOL
I'm planning on using one of the digital outputs to tell the PLC to abort when a jam occurs. This will prevent 150 eggs from being forced through out of position chains.
I've discovered this drive has a torque overload sensing ability that is gated by a user set time. If the torque exceeds a certain amount for longer than a certain time the drive will close a contact.
Does this drive actually know what the torque is?? Or is this really the same as the current?
Technical manual link for it: (15MB)
Keith Cress
kcress -