If a Transformer is listed at 12470Y/7200 Primary and 480Y/270 secondary (Shown AS 12470Y/7200V for primary and 480Y/270 secondary) does this mean the primary must be wired in a Y configuration if to be used at 12470 V and if you use a neutral on the primary then it would be 7200 V? With the Y being beside 12470 does this mean it cannot be used to replace an existing Delta-Wye wired transformer?
I am trying to replace an existing 12,470 pri/480/270 sec Xfmr that I am told is in a delta/Wye configuration but have not been able to go out and check yet.
You have not given the kVA rating (size) of the rating. But I am sure that the primary is connected as WYE at the factory
and it is not that easy to change it. Since, each primary winding voltage rating is 12470V/(1.732)=7200V, one cannot
increase that voltage so that voltage per turn is not exceeded. Therefore, you cannot connect primary to 12470V DELTA.
The transformer is essentially a YNyn transformer with (L-L) voltage ratio 12470/480V.
This cannot replace a Dyn transformer for two reasons:
1) Each of the primary windings is rated for 7200V (L-N) and not for 12470V that would be the case in case of Delta primary.
2) The YNyn transformer has no phase shift between primary & secondary, unlike Dyn transformer. This may or may not be relevant depending on your power system configuration.
RRaghunath Wouldnt the 12,470Y mean its Wye connected 12,470 Line to Line and the 7200 mean its Wye connected Line to Neutral?
Kiribanda I am trying to follow you. I see that you cant connect to 12,470 Delta but I believe you could for Wye if wired Line to Line and the 7200 would be if wired Line to Neutral? Or am I thinking of this incorrectly?
I am not sure whether I understood your concern correctly. If your supply voltage
is 12470V 3-ph, 3Wire, then you donot have a NEUTRAL to connect to the STAR point
of the primary. In any case to use this transformer you need 12470V/ 3-ph/ 4Wire
power supply otherwise you are going to float the neutral which will create other
problems.
"does this mean it cannot be used to replace an existing Delta-Wye wired transformer?" It depends on other system factors.
Since a Yg-Yg transformer will pass zero-sequence currents from low to high, and a D-Yg transformer won't, the rest of the system needs to be considered.
Most Yg transformer must be grounded, or the reduced insulation near the neutral could breakdown. So without more information, I think that you can't float the neutral. Do you have a system ground on the high side?
Typically 12470V systems are grounded and the utility does not necessarily provide a neutral conductor but this is something you need to confirm with the serving utility. Many times these systems are multi-grounded and I prefer to use concentric neutral conductors and ground the concentric neutrals on both ends - at the transformer and the source feeding it. The transformer HO bushing should also be grounded.
"Throughout space there is energy. Is this energy static or kinetic! If static our hopes are in vain; if kinetic ù and this we know it is, for certain ù then it is a mere question of time when men will succeed in attaching their machinery to the very wheelwork of nature". û Nikola Tesla