I hate to assume your question wasn't answered correctly yet, but a wye-start, delta-run motor starter usually has one set of overloads, for the delta-run only.
If it is this type of motor, then you must have six leads. You should have one nameplate FLA for the delta connection. The overloads are based on the nameplate FLA at the correct voltage (delta) connection. Typically, most people end up using values slightly higher for the overloads to avoid nuisance tripping.
If you're interested in the actual current, the wye connection has a voltage applied to each winding which is 0.577 times the delta connection voltage, which allows a starting current of about 1/3 of the current when the full voltage is applied.
Per the NEC, for your motor, 3 phase/600V/100hp, FLA is 99A(actual table 430.150 voltage is 575V). Starting current varies depending on the Design letter, but design B,C, and D are 580A, meaning the wye-start current would be about 193A. Hope this helps.