You can check the truss shop drawings for anticipated uplift on the truss ends, or simply develop your own calculation. Commercially available straps may be satisfactory depending on the loads. Multi-ply girder trusses or long span trusses usually seem to have the largest uplifts.
boo1 made a good suggestion, make sure that the truss is not directly on the masonry unless it is made of treated wood (highly unlikely unless it was specified). You can best break this with a treated sill, or as his attached sketch shows with a moisture barrier such as a steel sill.
With the higher heel height on the new truss will you now need to have the last course of masonry be cut to match the top chord elevation of the existing structure? If that is accurate, then perhaps you could cut the last course by an additional 1.5" to allow for a continuous sill. Of course, if the contractor is still opposed to this detail you still have the steel barrier option (and I imagine others as well).
There are several good manufactures of truss clips available, but I happen to have a Simpson Strong-Tie catalog right here. The 2006 version I have shows many good applications for roof trusses bearing on masonry walls.
You can download their current literature here...
Pages 139-147 address attachment to masonry.
If that link fails, simply go to their homepage at
I agree with several contributors that truss blocking (picture frame blocking or solid wood depending on the heel depth) would be required to transfer lateral loads into the masonry wall. Don't forget to specify the nailing into the blocking and follow your shear path all the way through.