For those of you wondering about the need for shrinkage compensation devices or careful control of wood moisture content with wood shear walls, consider my recent experience with a multi-story wood building in the Seattle area. The siding on the building had buckled as much as 1 3/8" --- always at the rim joists in upper stories --- in several places. The owner was quite concerned that the rims might be decaying or ???
In fact, the shrinkage at just the top and bottom plates (double plate on lower wall, single sole plate at upper) adds up. With 4 1/2" of wood at 4 percent shrinkage (see Design of Wood Structures, by Breyer, Findley, Pollock, Cobeen) the total is .18" . Shrinkage could be up to 6%, which would be 0.27" of shrinkage. Breyer, Findley, Pollock, and Cobeen note that 6% shrinkage was recommended by Rummelhardt and Fantozzi, "Multistory Wood-Frame Structures: Shrinkage Considerations and Calculations," 1992 ASCE Structures Congress.
So .... even if the joists do not shrink (TJIs can be pretty stable, but not necessarily) with a depth of 19" across the rim, nail to nail, (the building in question had a rim and TJs of 18" depth ) the shrinkage is enough to buckle the strap about 1 3/8". If you don't believe it (closed form solution with chords and segments of circles not available) draw it to scale with a CAD program.
The result is not only siding damage, but a very loose and ineffective strap. More than about 1/8" slop is too much.
This is far different than the conclusions that I saw in thread507-339808 .... but I do see a lot of wood, and it does crazy stuff. It is also in line with some things I learned at a Structural Engineers Assn of WA seminar years ago .... too bad I no longer have the notes to reference them.
Be careful
In fact, the shrinkage at just the top and bottom plates (double plate on lower wall, single sole plate at upper) adds up. With 4 1/2" of wood at 4 percent shrinkage (see Design of Wood Structures, by Breyer, Findley, Pollock, Cobeen) the total is .18" . Shrinkage could be up to 6%, which would be 0.27" of shrinkage. Breyer, Findley, Pollock, and Cobeen note that 6% shrinkage was recommended by Rummelhardt and Fantozzi, "Multistory Wood-Frame Structures: Shrinkage Considerations and Calculations," 1992 ASCE Structures Congress.
So .... even if the joists do not shrink (TJIs can be pretty stable, but not necessarily) with a depth of 19" across the rim, nail to nail, (the building in question had a rim and TJs of 18" depth ) the shrinkage is enough to buckle the strap about 1 3/8". If you don't believe it (closed form solution with chords and segments of circles not available) draw it to scale with a CAD program.
The result is not only siding damage, but a very loose and ineffective strap. More than about 1/8" slop is too much.
This is far different than the conclusions that I saw in thread507-339808 .... but I do see a lot of wood, and it does crazy stuff. It is also in line with some things I learned at a Structural Engineers Assn of WA seminar years ago .... too bad I no longer have the notes to reference them.
Be careful