Wood Post on 2X bottom Plate

Status
Not open for further replies.

NewbieStruct

Structural
May 31, 2011
101
We have a situation where the contractor put a wood post taking 4 kips of load directly unto a 2x wood plate ? I am trying to figure out if this wood crush the wood plate? Is this compression perpendicular to grain ?

 
Replies continue below

Recommended for you

Yes, although "crushing" is relative.
It is.
 
So how do you verify if it works. Are there any factors that I need to use?
 
Well Fc perpendicular to grain is 565 psi. That gives me a required area of 7.07 square inches. The wood post is 4x4 (12.25 square inches). Am I missing any factors?
 
3.5x3.5 actually for today's lumber. 12.25 is correct
315 paid peso. Should be OK depending on species.

Mike McCann
MMC Engineering

 
315 psi should be OK... sheeeesh! Darn cell..

Mike McCann
MMC Engineering

 