Are the wind loads shown the uplift without factoring in dead load? If so it looks like you wouldn't have any net uplift and I would just use a 2-2x nailer bolted into the beam and attach the trusses with either toenails or a Simpson connector if you feel like it, the H2.5A is probably the most common. If those uplift loads are net uplift after factoring in dead load, 1.6k is pretty high so it might be better to use a Simpson column cap welded to the top of the steel beam, this is preferable to fabricated steel with bolts because the Simpson connectors use self driving screws and dont reduce the section depth of the truss chord, which will have a high tension load in it.
If it were me, if I'm using a steel beam I would just use some 3" pipe columns at each end and weld directly to the bottom of the beam. Another option would just be to go all wood with a glulam beam and attach the beam and column with a Simpson column cap with adequate uplift capacity, would also simplify the truss connections. If you really need to go steel/wood then I guess you could fabricate plates or angles onto the bottom of the beam and bolt into the column, you would need to place the bolts a minimum of 4 diameters from the top of the column for partial uplift capacity and 7 diameters for full uplift capacity.