- Aug 29, 2009
- 7
What is the code/norm that allows using a 2 pole contactor in a 3 phase application? (leaving one line "hot", not interrupted)
Thanks
Thanks
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
430.84 Need Not Open All Conductors.
The controller shall not be required to open all conductors to the motor.