Wiring magnetic contactors 1

Status
Not open for further replies.

REC67

Electrical
Aug 29, 2009
7
What is the code/norm that allows using a 2 pole contactor in a 3 phase application? (leaving one line "hot", not interrupted)

Thanks
 
Replies continue below

Recommended for you

The 2008 NEC says:
430.84 Need Not Open All Conductors.
The controller shall not be required to open all conductors to the motor.
 
Associated side note however:

All 3 phases must have overload protection.


"If I had eight hours to chop down a tree, I'd spend six sharpening my axe." -- Abraham Lincoln