Air is the key. If you are pouring, standard air should not be a problem. If you are pumping, air can become a problem. Talk to the contractor and pump truck sub about maintaining air. If this is a job that is being put out to bid talk to reputable contractor and pump truck operator you know.
As for ACI 306R, I am not a fan of prolonged heating. Unless the pour is very small, insulating with concrete blankets should be okay for 20-40 degree. (F) Heating often does more damage than good. Note though in cold weather, once you get past about 500 psi, the concrete usually can resist freezing, however strength gain is significantly retarded, so if you need strength right away, you may need to heat. Retarded strength due to cold weather was the cause of a nasty jump form failure at Willow Island many years ago.