Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations JStephen on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Wind speed for fire fighting Model

Status
Not open for further replies.

zishan99

Mechanical
Joined
Mar 11, 2006
Messages
15
Location
GB
Which wind speed (average or maximum)will considered for model an oil terminal fire fighting system.What is the limit of wind speed to be considered.
 
I would be inclined to use the maximum wind speed which has been recorded historically for fifty (50) years at the location of the plant. For a measure of comfort, I would then use an additional ten (10) percent.

This would represent the worst case scenario in your model and drive the design to handle for maximum loads.

Just my two (2) cents worth.

Kenneth J Hueston, PEng
Principal
Sturni-Hueston Engineering Inc
Edmonton, Alberta Canada
 
I'd have thought your insurance company would have an opinion on the matter.

Cheers

Greg Locock

Please see FAQ731-376 for tips on how to make the best use of Eng-Tips.
 
Worst case has to be rotor wash from news helicopters.



Mike Halloran
Pembroke Pines, FL, USA
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top